iggy2
Senior Member
- Location
- NEw England
Article 800 cables, installed in a chapter 3 wiring method (PVC conduit) - raceways must be installed to comply with Chapter 3. If cables are buried, in PVC conduit, under a "street, highway, road, alley, driveway or parking lot", 24" cover is required per table 300.5, 5th row down.
1) If 24" cover cannot be had, can 2" of concrete be added over the top, and the raceway - which is still under a "street, highway, road, alley, driveway or parking lot", - be installed per row 2 of the table? (I do not see that row 2 can apply to a situation which is under a "street, highway, road, alley, driveway or parking lot"... only the 5th row addresses that situation. In other words, you do not get to pick which row you want to use. You pick the row that applies to your situation. Conversely, I do not then know how to install a conduit under a paved, vehicular area with less than 24" cover.)
2) If yes to 1 above, would the paving (assuming it's is at least 2" thick, binder and finish, constitute the "2" thick concrete or equivalent"?
Thanks.
1) If 24" cover cannot be had, can 2" of concrete be added over the top, and the raceway - which is still under a "street, highway, road, alley, driveway or parking lot", - be installed per row 2 of the table? (I do not see that row 2 can apply to a situation which is under a "street, highway, road, alley, driveway or parking lot"... only the 5th row addresses that situation. In other words, you do not get to pick which row you want to use. You pick the row that applies to your situation. Conversely, I do not then know how to install a conduit under a paved, vehicular area with less than 24" cover.)
2) If yes to 1 above, would the paving (assuming it's is at least 2" thick, binder and finish, constitute the "2" thick concrete or equivalent"?