What do you think?
I've got a 5kV duct bank running under a road. Excavation of that road has revealed a sewer line at a depth of 38 inches (to the top). If we were to put our 16 inch tall ductbank directly on top of it, we'd be left with 22 inches.
a) what do we need for a buffer between the two utilities and can we/should we use some kind of expansive material?
b) baring going deep (which is feasible), the contractor has suggested and even had blessed by the local AHJ, pouring 6 inches of concrete around the duct bank in lieu of 3. So another 3 inches on the bottom, another 3 inches on the top leaving the top of the duct bank (assuming 3 inch buffer between utilities) about 11 inches.
I'd be interested in your collective experience on the matter and whether or not you think I should accept it?
I've got a 5kV duct bank running under a road. Excavation of that road has revealed a sewer line at a depth of 38 inches (to the top). If we were to put our 16 inch tall ductbank directly on top of it, we'd be left with 22 inches.
a) what do we need for a buffer between the two utilities and can we/should we use some kind of expansive material?
b) baring going deep (which is feasible), the contractor has suggested and even had blessed by the local AHJ, pouring 6 inches of concrete around the duct bank in lieu of 3. So another 3 inches on the bottom, another 3 inches on the top leaving the top of the duct bank (assuming 3 inch buffer between utilities) about 11 inches.