Several of us are having a discussion concerning the required cover over a duct bank. A colleague's email sums the discussion up best:
"We are trying to determine the minimum depth we can run a concrete encased 600 volt duct bank under a plant roadway. Article 300.5 and Table 300.5 address direct buried conduits and conduits with a concrete slab over top, but does not appear to address concrete encased ductbanks. One of my staff members understands from Table 300.5 the ductbank needs to be 24inchs deep under the driveway (although there is no column in the table for concrete encased conduit), whereas I had always understood concrete encased ductbanks could even be flush with the ground or driveway."
Opinions?
thanks
jim
"We are trying to determine the minimum depth we can run a concrete encased 600 volt duct bank under a plant roadway. Article 300.5 and Table 300.5 address direct buried conduits and conduits with a concrete slab over top, but does not appear to address concrete encased ductbanks. One of my staff members understands from Table 300.5 the ductbank needs to be 24inchs deep under the driveway (although there is no column in the table for concrete encased conduit), whereas I had always understood concrete encased ductbanks could even be flush with the ground or driveway."