Covering a junction box with drywall

Status
Not open for further replies.
TypeA said:
Are there circumstances were a junction box can be covered by drywall?



There are many, and I mean many "circumstances" where Jboxes are covered...none of them in my mind are justified.

I worked in many old buildings of different types of occupancies, and I can tell you there are always ways to resolve this. It takes creativity and a little more $.
 

iwire

Moderator
Staff member
Location
Massachusetts
petersonra said:
yes. if there are no splices or other connections inside it.

If 'it'* has a removable cover and contains any circuit conductors it must not be covered by drywall or and finish.


*conduit bodies, other fittings, boxes, wireways etc.
 

480sparky

Senior Member
Location
Iowegia
Article 314, covering Outlet,, Device, Pull, and Junction Boxes, et al, are in Chapter 3.
Chapter 3 is titled Wiring Methods and Materials, and has been since at least 1940, my oldest Code book.
Accessible (as applied to wiring methods), is defined in Art. 100 as "Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building." Wording is extremely similar to 1940 NEC.

So, no, it cannot be buried in the wall.
TypeA said:
Are there circumstances were a junction box can be covered by drywall?
However, the true answer to the question is:
Yes, if the person hanging the drywall is not an electrician.
 
Last edited:

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Hey 480,

We must have went to the same school! I have 20 oz. framing hammer that I brandish, as I'm making my favorite comment to a rocker "you can find, or I can find it, doesn't matter to me!" Wiped that stupid grin right off the last guys face when he saw me wrapping up to hit the wall, and he started shouting Okay, Okay, some people have no sense of humor!"

Yes I have a sense of humor, I also respect the dollars and efforts of electrical work.
 