Covering over electrical heat tape on water pipes

Status
Not open for further replies.

teejer

Member
We manufacture a plastic covering used by utility companies to cover risers on poles. This item is not affected by the NEC since it is made for utility use, so the covering is not Ul listed. A non-utility customer found us on the internet and is looking to use our covering over electrical heat tape on water pipes. This is the type of tape that is plugged in an there is a heating element that keeps water pipes from being frozen. The customer wants to use the plastic covering to insulate and protect his pipes. My first thought is to say no to this application because of potential fire risk due to the fact that this covering is not flame retardant, but others I work with don't think it is a big deal, since not much heat is generated by the tape, just enough to keep water flowing. Does anyone have any thoughts on this?
 

realolman

Senior Member
You have to put signs on them warning of heat tapes in use.

427.13

Maybe you could print it right on your product:smile:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
petersonra said:
virtually all industrial pipe heat tape installs I have seen are insulated with fiberglass, and then plastic shields over that.


Us too. Some of the fiberglass insulation is 2" thick. Have also seen it wrapped in metal for exterior locations.
 

teejer

Member
Fire resistant insulation makes sense

Fire resistant insulation makes sense

Thanks for the replies. The heavy fire resistant insulation makes sense. I will pass the word on to the customer.
 
Read the label provided on the cable. I was on a job the other day and the label directed the installer to keep the cable exposed for its entire length. I do not know if this is for all cable. This cable was supplied by cord and plug connection.
 

realolman

Senior Member
Pierre C Belarge said:
Read the label provided on the cable. I was on a job the other day and the label directed the installer to keep the cable exposed for its entire length. I do not know if this is for all cable. This cable was supplied by cord and plug connection.

I wouldn't use that cable. That doesn't make any sense. That would kinda defeat the purpose.
 
Last edited:
Pierre C Belarge said:
Read the label provided on the cable. I was on a job the other day and the label directed the installer to keep the cable exposed for its entire length. I do not know if this is for all cable. This cable was supplied by cord and plug connection.

That is nonsense.

Heat tracing is designed to keep the mateiral inside the pipe at the desired tempearture. To accomplish this without insulation one would need 50-60 times the wattage per foot of what ordinary heat tracers are designed to do. They are ususally 3-5 W/ft and require 1/2" thinck neoprene or fiberglass insulation. They are "make-up" of the heat loss that occurs accross the insulation thinckness. It is such a low temperature that fire hazard does not exist.

However. Make sure that you are installing a special GFCB - high leakage current 30-40mA - designed for heat tracing and that you have a braided metallic overjacket on the tracer that is properly grounded.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Pierre C Belarge said:
Read the label provided on the cable. I was on a job the other day and the label directed the installer to keep the cable exposed for its entire length. I do not know if this is for all cable. This cable was supplied by cord and plug connection.

i think this is for the kind of heat tape used to melt ice dams on your roof.
 

masterelect1

Senior Member
Location
Baltimore
Melting??

Melting??

petersonra said:
i think this is for the kind of heat tape used to melt ice dams on your roof.

I have never dealt with heat tape that had the capability to melt frozen materials. When a freeze up occurs due to heat tape failure or power loss, in the applications I have seen, it was necessary to manually defrost the freeze up and then to repair/re-energize the tape.
 
masterelect1 said:
I have never dealt with heat tape that had the capability to melt frozen materials. When a freeze up occurs due to heat tape failure or power loss, in the applications I have seen, it was necessary to manually defrost the freeze up and then to repair/re-energize the tape.

Both of you are correct.

There are heat tapes designed to prevent ice buildup on roof edges/overhangs although I more often see them forming triangular patches of iceblocks than completely repventing the formation of ice. (You would need to have a continous heat panel for the later.)

Heat tracing is normally applied for the maintenance of process temperature of pipelines or vessels. The tracing heat output is designed to make up for the heat loss occuring through the selected insulating material. However, whenever the heat output of the tracer exceeds the heat loss, the material in the pipe and the pipe will heat up until heat equilibrium is reached, eg. the heat loss through the insulation will equal the output. (Insulating material have different heat losses at different temperatures.) Consequently it is possible to heat up material, but it takes a long, long, long time. If unfreezing the pipes required, extra heat tracing of multiple runs of tracers applied or two tracers of different rating used.

Using heat tracing in Hazardous Areas contains a full set of additional problems and issues that needs to be addressed.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
weressl said:
There are heat tapes designed to prevent ice buildup on roof edges/overhangs although I more often see them forming triangular patches of iceblocks than completely repventing the formation of ice.
Since the idea is to prevent water infiltration from ice damming, this is usually adequate.
 