Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
I have a computer room AC that's 25.4 FLA. It has a 30A disconnect, a 50A breaker with 3 #6's. Sizes seem screwy.
I come up with:
1st step - For conductors 25.4 x 125% = 31.75A. So #10 THHN would be fine
2nd step - Breaker size - Not sure of calc. I believe it should be 125% of continuous load. 40A breaker would work.
3rd step - Disconnect size would be 115% of FLA. 30A disconnect.
Correct?
I come up with:
1st step - For conductors 25.4 x 125% = 31.75A. So #10 THHN would be fine
2nd step - Breaker size - Not sure of calc. I believe it should be 125% of continuous load. 40A breaker would work.
3rd step - Disconnect size would be 115% of FLA. 30A disconnect.
Correct?