M Mitch Lecour New member Location long beach CA Apr 10, 2018 #1 I have an A frame crane being installed. The crane is being fed from a distribution panel 20 ft away. Do I still need a fused disconnect or is using the breaker sufficient?
I have an A frame crane being installed. The crane is being fed from a distribution panel 20 ft away. Do I still need a fused disconnect or is using the breaker sufficient?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 10, 2018 #2 If I read 610.32 correctly, the breaker may be used as the disconnect. See Section 610.42 as to the rating requirements.
If I read 610.32 correctly, the breaker may be used as the disconnect. See Section 610.42 as to the rating requirements.