heath harry
Member
We have two separate cranes in separate bays being fed from 480 volt switchgear located in an electric room. We showed a 2000 amp and 1600 amp disconnect located in each bay in line of sight from the cranes. Article 610.31 of the NEC states as follows:
610.31 Runway Conductor Disconnecting Means. A disconnecting means that has a continuous ampere rating not less than that computed in 610.14(E) and (F) shall be provided between the runway contact conductors and the power supply. Such disconnecting means shall consist of a motor-circuit switch, circuit breaker, or molded case switch. This disconnecting means shall be as follows:
(1) Readily accessible and operable from the ground or floor level.
(2) Capable of being locked in the open position.
(3) Open all ungrounded conductors simultaneously.
(4) Placed within view of the runway contact conductors.
Does a Pringle disconnect Switch meet this code article since it has to consist of a motor-circuit switch, circuit breaker, or molded case switch. If not what type of switch should be installed. If the breaker in the electric room is lockable does a disconnect even have to be installed?
[ August 11, 2003, 03:38 PM: Message edited by: heath harry ]
610.31 Runway Conductor Disconnecting Means. A disconnecting means that has a continuous ampere rating not less than that computed in 610.14(E) and (F) shall be provided between the runway contact conductors and the power supply. Such disconnecting means shall consist of a motor-circuit switch, circuit breaker, or molded case switch. This disconnecting means shall be as follows:
(1) Readily accessible and operable from the ground or floor level.
(2) Capable of being locked in the open position.
(3) Open all ungrounded conductors simultaneously.
(4) Placed within view of the runway contact conductors.
Does a Pringle disconnect Switch meet this code article since it has to consist of a motor-circuit switch, circuit breaker, or molded case switch. If not what type of switch should be installed. If the breaker in the electric room is lockable does a disconnect even have to be installed?
[ August 11, 2003, 03:38 PM: Message edited by: heath harry ]