Razzap
Member
Recently my company built an addition, and extended the overhead crane rail approximately 300 feet. The original crane rail was about 400 feet, for a total of 700 feet. The original building is fed from a 480 V, 3 phase Y -Y transformer. The new addition is fed from a 480 V, 3 phase Y-Delta transformer. Both primaries are fed from the same POCO. The two crane rails were not electrically connected together, but when the crane traveled across the gap, the forward shoes were in contact with the new system, while the back shoes were in contact with the original system. Sparks flew and the main breaker tripped out at the original building. The electrical contractors checked phasing between the original and new crane rail and it was determined that phasing was OK. My question is, what went wrong? I am thinking that it might have something to do with transformer polarity, but I cannot seem to find much info on the Web. The electrical contractor is now saying that they will have to replace the new Y-Delta tranny with a Y-Y. From what I have read, paralleling 3-phase transformers does not work because of polarity issues. When the crane bridged the gap between original and new, it effectively put the transformers in parallel. Also, it seems that phase B original and phase B new have about 144 V between them, measured at the crane rail. I am not really involved in this dilema, but just an electrician, building machine tools and watching everyone scratching their heads over this problem. Any ideas on how to solve this?