Member
I would like to know what people think of locating a conductor rail disconnect switch inside of a guarded area.
Specifically, if the area is guarded by a fence.
The equipment in question would be:
#1 Automatic transfer vehicles that run on a traveling rail that has conductor rails on ground level. It is guarded by a fence. Can the disconnect switch be located inside the fence?
#2. Automated storage and retrieval machine on a traveling rail that has conductor rails on ground level. It is guarded by a fence. Can the disconnect switch be located inside the fence?
I do not see how this is readily accessible or safe.
I reference
NEC article 610 Part IV.
Disconnects shall be
1) Readily accessible.
2) Capable of being locked in the open position.
3) Open ALL ungrounded conductors simultaneously.
4) Placed within view of the runway contact conductors.
Article 100
Readily accessible : "Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth."
Within view: "... the specified equipment is to be visible and not more than 15m (50ft) distant from the other"
Specifically, if the area is guarded by a fence.
The equipment in question would be:
#1 Automatic transfer vehicles that run on a traveling rail that has conductor rails on ground level. It is guarded by a fence. Can the disconnect switch be located inside the fence?
#2. Automated storage and retrieval machine on a traveling rail that has conductor rails on ground level. It is guarded by a fence. Can the disconnect switch be located inside the fence?
I do not see how this is readily accessible or safe.
I reference
NEC article 610 Part IV.
Disconnects shall be
1) Readily accessible.
2) Capable of being locked in the open position.
3) Open ALL ungrounded conductors simultaneously.
4) Placed within view of the runway contact conductors.
Article 100
Readily accessible : "Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth."
Within view: "... the specified equipment is to be visible and not more than 15m (50ft) distant from the other"