Crawl space wiring NM-B or UF

nizak

Senior Member
I’m doing a new build with a crawl space.
- Floor poured concrete
-Humidity sensing / air quality maintained

AHJ is calling it a potentially damp location and wants UF cable run in that area.

I’ve already pulled my home runs and 10 or so travel thru the crawl.

Could see his point if the environment was different. I’ve never encountered this.

FYI . I’m an out of towner working in an area I’ve never been in before. He made reference to me being new to the area.
 

farmantenna

Senior Member
Location
mass
"Potentially damp location"? If the humidistat or dehumidifier fails? Because you said it's a conditioned space. I've seen such crawl spaces very dry and some old cottages with sand floor and no insulation disgustingly wet.

you have no choice with this inspector. Feel sorry for you. You'll probably go back on the finish and observe a beautifully dry crawl space.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
If you're not going to go back to that area burn that bridge.
Go to the state level and have them enforce code only.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
AHJs around here consider crawl spaces as wet locations, no exceptions or circumstances.
Really? What part of the SF Bay Area?

My experience is only Berkeley, and they take the reasonable view that crawl spaces are dry. Calling it a wet location is crazy, if it's raining in your crawl space, you have huge problems.

Cheers, Wayne
 

david

Senior Member
Location
Pennsylvania
The residential building codes have required ventilation of crawl spaces.

When warm humid outside air mixes through vents to the outside with the cooler air in a crawl space you have condensation.

I've been in crawl spaces where the fiber class insulation in the floor joists where soaking wet and the water dripping all over you.

Lately the building codes have allowed sealing these spaces and having the air conditioned in them the same as you would other livable areas in your home

This approach is said to deal with the condensation issues in a crawl space
 

nizak

Senior Member
The residential building codes have required ventilation of crawl spaces.

When warm humid outside air mixes through vents to the outside with the cooler air in a crawl space you have condensation.

I've been in crawl spaces where the fiber class insulation in the floor joists where soaking wet and the water dripping all over you.

Lately the building codes have allowed sealing these spaces and having the air conditioned in them the same as you would other livable areas in your home

This approach is said to deal with the condensation issues in a crawl space
It will have a system in place to deal with humidity issues. Not certain of the brand/ model, etc.
 

david

Senior Member
Location
Pennsylvania
It will have a system in place to deal with humidity issues. Not certain of the brand/ model, etc.
Havnt talk to the building inspector about this in a few years, but I think here you eather vent the space with outside air or you insulated it and have your duct work for your furnace/air into that space. I think the other option was insulated and open to conditioned interior spaces
 

kwired

Electron manager
Location
NE Nebraska
AHJs around here consider crawl spaces as wet locations, no exceptions or circumstances.
Which is stupid. If it is wet you likely will have mold issues, the idea is to make them so they will be dry unless something abnormal happens like a pipe bursting, but that is a temporary condition then it supposed to get dry again.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
AHJs around here consider crawl spaces as wet locations, no exceptions or circumstances.
Which AHJ's? I have never run into any. What do they require for floor framing, sub floor, insulation and duct work?

The dirt may get wet but not the framing above. If the floor structure above is wet you have much bigger problems than NM cable getting wet.
 

acin

Senior Member
Location
pacific grove california
Occupation
general building contractor est.1984 . C 10 elec. lic.as of 8 / 7/ 2020
I’m doing a new build with a crawl space.
- Floor poured concrete
-Humidity sensing / air quality maintained

AHJ is calling it a potentially damp location and wants UF cable run in that area.

I’ve already pulled my home runs and 10 or so travel thru the crawl.

Could see his point if the environment was different. I’ve never encountered this.

FYI . I’m an out of towner working in an area I’ve never been in before. He made reference to me being new to the area.
can you box it with wood or plywood ?
 

nizak

Senior Member
If he considers it a wet location, the floor joists must be pressure treated! LOL!
I spoke with the head of inspections for the Township and he overrode the inspectors call .

I said I hoped his reason for not approving my work was because I was not a local contractor.

He smirked and said I don’t think it was..
 