I inspected a 4 meter service upgrade yesterday. The electrician ran SEU cable from the meter sockets 15ft. through a shallow crawlspace to the main service disconnects.
I asked him why he didn't put the main disconnects outside and run 4 wire SER cable to the service panels. He said that the cable was not subject to damage because of the shallow crawlspace and should be considered outside the building, and NEC 230.70(A)(1) should not apply.
I think his first mistake was not to call me before doing the work, but that is another story.
Changing this would be a considerable expense to the contractor, that I do not want to cause him, as long as the service is safe and code compliant.
I think that he has a good point about the cable not being subject to damage. The question is are they really outside the building? I am sure some of you have seen this situation before
Commentary in the NEC HANDBOOK says " No Maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this code has the responsibility for, and is charged with, making the decision as to how far inside the building the service entrance conductors are allowed to travel to the main disconnecting means.
Ok guys be the inspector, what is your decision? Opinions appreciated.
I asked him why he didn't put the main disconnects outside and run 4 wire SER cable to the service panels. He said that the cable was not subject to damage because of the shallow crawlspace and should be considered outside the building, and NEC 230.70(A)(1) should not apply.
I think his first mistake was not to call me before doing the work, but that is another story.
Changing this would be a considerable expense to the contractor, that I do not want to cause him, as long as the service is safe and code compliant.
I think that he has a good point about the cable not being subject to damage. The question is are they really outside the building? I am sure some of you have seen this situation before
Commentary in the NEC HANDBOOK says " No Maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this code has the responsibility for, and is charged with, making the decision as to how far inside the building the service entrance conductors are allowed to travel to the main disconnecting means.
Ok guys be the inspector, what is your decision? Opinions appreciated.