L linwue Member Location Minnesota Occupation Electrician Apr 27, 2005 #1 tap conductor? What would the tap cond. size be if I were feeding a 100 amp panel from a 600 amp disconnect,distance is less than 25ft. Any help?
tap conductor? What would the tap cond. size be if I were feeding a 100 amp panel from a 600 amp disconnect,distance is less than 25ft. Any help?
bob Senior Member Location Alabama Apr 27, 2005 #2 Re: crazy bout tap conductors Read 240.21.B2 and try to work out an answer. Come back with the answer an we will help you determine the conductor size if you are incorrect.
Re: crazy bout tap conductors Read 240.21.B2 and try to work out an answer. Come back with the answer an we will help you determine the conductor size if you are incorrect.
L linwue Member Location Minnesota Occupation Electrician Apr 27, 2005 #3 Re: crazy bout tap conductors I come up with a 3/0.I took 1/3 of 600amps which is 200amps which I believe would be a 3/0
Re: crazy bout tap conductors I come up with a 3/0.I took 1/3 of 600amps which is 200amps which I believe would be a 3/0