Atxrl1983
Member
- Location
- Austin tx USA
Ok so this is what I have. Simple 480/277 panel feeds trans which feeds a 120/208 LV panel. 3phase. All breakers off I get 120v hot to ground and 120v hot to neutral on feeders. All breakers on I get 110v a-phase to ground, 124v b-phase to ground, and 135v c-phase to ground to feeders. I have receptacles reading 120v hot to neutral. And 208v neutral to ground. I found this today. Did not have time or ladders to really look into it. Nothing is tripped. But 2 power surges were burnt. I'm actually excited to see what causes this. It is in the office of the GC of a new 19 story I am running. Still a hole in the ground. I wasn't sure where to post this. Let me know what y'all think.