NEC states spaces adjacent to class 1, div 1, group D locations is a Class 1, Div 2, Group D location.
On a sanitary lift station project, we are looking to declassify an electrical space without providing ventilation per NFPA 820. See left side diagram of attached sketch for existing conditions.
We thought of sealing the door in the wall between the wetwell and electrical room (refer to space designations on attached sketch), but per NEC the electrical room would still be adjacent to a class 1, div 1 location, thus making it class 1, div 2.
What if we build a dual wall system? See right side of attached sketched. Red lines are proposed.
If we construct a new wall in the wetwell side, say 6-12" from existing wall shared with the electrical room and by doing so creating a new void or space. Then the void would be Class 1, Div 2, and now since the electrical room wall is shared with the new void space, the electrical room is now adjacent to a class 1, div 2 location, and such the electrical room wouldn't be classified.
This seems like a fairly simple solution but I have never seen this done before. I am wondering what I might be missing?
On a sanitary lift station project, we are looking to declassify an electrical space without providing ventilation per NFPA 820. See left side diagram of attached sketch for existing conditions.
We thought of sealing the door in the wall between the wetwell and electrical room (refer to space designations on attached sketch), but per NEC the electrical room would still be adjacent to a class 1, div 1 location, thus making it class 1, div 2.
What if we build a dual wall system? See right side of attached sketched. Red lines are proposed.
If we construct a new wall in the wetwell side, say 6-12" from existing wall shared with the electrical room and by doing so creating a new void or space. Then the void would be Class 1, Div 2, and now since the electrical room wall is shared with the new void space, the electrical room is now adjacent to a class 1, div 2 location, and such the electrical room wouldn't be classified.
This seems like a fairly simple solution but I have never seen this done before. I am wondering what I might be missing?