Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
I have to install a temp hookup to a job trailer. The panel is 20 feet inside the building, then extend down underground to the trailer location. I obviously want to do it in the cheapest way possible. My thought is to use SEU cable for the entire run. Southwire says their SER is rated as type SE cable for installation in wet and dry locations, above ground. But the conductors are also rated THWN. I don't see any reason why I can't run it overhead inside the building unprotected, then in a conduit sleeve down the outside, underground in conduit, and up under the trailer, then exposed under the trailer with a short stub up to the exterior panel protected again by conduit.
My feeling is that underground it is still THWN in conduit so that would be legal, even though SER underground is not. Then all other locations it is SE not subject to damage wet or dry location.