Crimp connectors 250 kmil alum

ronball

Member
Location
Champaign Il.
Occupation
Electric Contractor
I have to pig tail off to 3 separate service from my continuos GEC to 6 " water pipe.
what type of non removal crimps can be used" can I crimp them together in a 500 kmil crimp connector, or is their any such thing
as a TEE crimp... Thx
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes there are crimp style T taps or C taps but as Larry stated since you are installing bonding jumpers the connection to the GEC is not required to be irreversible. A split bolt listed for Aluminum conductors or Cu/Al if you jumpers are copper is all that's required.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
My Inspector said they had to be irreversible. thats why I am looking for crimp crap!!!!
Tell him that he's incorrect. The GEC has to be irreversible spliced, bonding jumpers do not. Here's one example of the difference between the two.

119882d1515102700-gec-entering-enclosure-mike-holt-250-4.jpg
 