mshields
Senior Member
- Location
- Boston, MA
This question is unique to Massachusetts (and perhaps other states with similar requirements) which requires that all distribution equipment that is part of the Emergency System for a hospital be in dedicated 2 hour rated rooms (The requirement is actually an ammendment to Article 700 but is applicable to the critical branch per Article 517).
I've got a server room, designed to Article 645, for which the loads have been deemed Critical. Within the server room I've got acritical source panel and a normal source panel. All the loads served by these panels are within the room.
I'm wondering if this is a violation or not.
Appreciate any input.
thanks,
Mike
I've got a server room, designed to Article 645, for which the loads have been deemed Critical. Within the server room I've got acritical source panel and a normal source panel. All the loads served by these panels are within the room.
I'm wondering if this is a violation or not.
Appreciate any input.