Looked at a job today, customer wants electrical sys. (lights & recpt.s) in a show cattle barn. Some of these recpt.s are to supply power for blow dryers. Name plate on the blow dryers is as follows: 115 volts, 19 amps, 60 cycles.
These blow dryers are portable, with a SJTOW 3-12 cord & 15A/125V factory installed cord end. This equipment should be considered a continuous load. Table 210.21(B)(2) does not allow loads over 16A on a 20A crkt. or recpt. Table 210.21(B)(3) does not allow a 15A or 20A recpt. on a 30A crkt. The customer takes these blow dryers with him to stock shows, I could change out the cord end to a 30A cord end, but he probably won't be able to find a 30A/125V recpt. at a stock show. Also shouldn't the recpt. that these blow dryers plug into be GFCI-protected (either GFCI breaker or GFCI recpt.)? The floor in this barn is dirt. Any ideas or suggestions?
These blow dryers are portable, with a SJTOW 3-12 cord & 15A/125V factory installed cord end. This equipment should be considered a continuous load. Table 210.21(B)(2) does not allow loads over 16A on a 20A crkt. or recpt. Table 210.21(B)(3) does not allow a 15A or 20A recpt. on a 30A crkt. The customer takes these blow dryers with him to stock shows, I could change out the cord end to a 30A cord end, but he probably won't be able to find a 30A/125V recpt. at a stock show. Also shouldn't the recpt. that these blow dryers plug into be GFCI-protected (either GFCI breaker or GFCI recpt.)? The floor in this barn is dirt. Any ideas or suggestions?