Back in 2004 I got peripherally involved in an investigation of a fire at the Bellagio Hotel in Vegas (
http://m.lasvegassun.com/news/2004/apr/12/bellagio-blackout-creates-surreal-scene/).
It turned out to be that the concrete duct used for the service conductors was over filled, the bottom conductors over heated and caught fire. The ducts exceeded a 20% fill, but the drawings showed otherwise. What happened is that the main service conductors AND the conductors coming from the backup generators were put in the same duct. The drawings for each set showed them as separate, no fill violation, but the draftsman accidentally put the same duct number on both ducts, so the EC stuffed both runs in there. Then the inspector failed to notice it (or was paid off to look the other way when he found it, it is Vegas after all...). So when the main service conductors caught fire and the breaker tripped, the emergency power conductors, being in the same duct, ALSO caught fire and they had no power for about a week.