What available circuit breakers would be accepted replacements for the Crouse Hinds load center - picture of label is attached below.

From a 2002 UL letter (this forum) it looks like a Crouse Hinds MP breaker can be replaced by Murray Type MP-T.

Another UL letter posted here states that a Crouse Hinds Type MH-T breaker produced by Siemens is suitable for use in panels where Type MM breakers are specified. Would the still in stock Murray Type MH-T be accepted?

Thanks for any help,
Jim

link to better label picture
1993 Letter
2002 Letter

00-wLROFXf1yQj70WozaBtw87rDrQaVxFHDyHnimaUk2Qyxnn2H3SFQhTzOp6qITTxqldMTLfbtJ__wYVBQ_4iTow
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Don't need to see the letters. My go-to breaker for Crouse-Hinds would be BR breakers.

Remember, breakers are differentiated by type, not necessarily by manufacturer.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Don't need to see the letters. My go-to breaker for Crouse-Hinds would be BR breakers.

Remember, breakers are differentiated by type, not necessarily by manufacturer.
That panel label doesn't list BR as far as I can tell, the writing is sort of distorted. I always use Siemens or Murray and those are listed on the label.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Don't need to see the letters. My go-to breaker for Crouse-Hinds would be BR breakers.

Remember, breakers are differentiated by type, not necessarily by manufacturer.
Unless that un-readable label actually allows Type BR, it would be Siemens, according to master curt swartz.

10-08-03, 07:53 PM #4 curt swartz
Senior Member
Join Date: Feb 2003
Location: San Jose, CA
Posts: 944
Re: Circuit Breaker Compatibility
Crouse Hinds distribution equipment was renamed back to Murray when Siemens acquired the line. Murray breakers with the same part number can be used in Crouse Hinds equipment. Crouse Hinds equipment was named Murray before it was Crouse Hinds.

Cutler-Hammer acquired the Westinghouse distribution line which included Challenger. A Cutler-Hammer BR circuit breaker is the replacement for Westinghouse (Bryant) BR circuit breakers and Challenger C breakers. If you look at a BR breaker you will notice that it has both the Westinghouse and Challenger part numbers on it.
Curt Swartz
Electrical Contractor
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That panel label doesn't list BR as far as I can tell, the writing is sort of distorted. I always use Siemens or Murray and those are listed on the label.
Unless that un-readable label actually allows Type BR, it would be Siemens, according to master curt swartz.
It does. I've been here too long to post something like this without being sure. ;)

Look in the second line of #2, Bryant types, to the left of the Westinghouse "W" circle:

1655776491786.png
 

jimmyf1963

Member
Location
nyc
Occupation
technician
Sorry about the image. Thought I needed to upload pictures and attachments through links. Should have at least tried copy and paste.

Was told the condominium this is from was built in 1981. Will go with the Eaton BR line.

Thanks to all for the information.
 