Crouse hinds typr g Model 14 panelboard ?

Status
Not open for further replies.

awander

New member
I was at a house today, looking at a panelboard to give my opinion on whether it is installed and spec'dd properly.

The label on the inside of the enclosure cover indicates that it is a Crouse Hinds Model 14 Type G Panelboard.
This label also states "125A Maximum-see Main Breaker rating"
There is nothing else about the main breaker rating on the label. the Main breaker itself is a Type MO-A(if my old eyes didn't deceive me) 150A 2-pole breaker.
Further down on the label, it states that the panel board is for installation in box 77030-04(150A) or 77030-05(200A)

There is a label inside the box itself that says
Class CTL Enclosed Panelboard No DE-011652

My question is, is the 150A Main Breaker ok in this panelboard/enclosure?

I don't understand what the label means by saying "125A Maximum-see Main Breaker rating" and then going on to list separate box options for 150A and 200A.

I looked on the Cooper crouse hinds site and found nothing that even mentions this panelboard.

Andy
 