Hi all,
I am aware that UL is accepted across US as well Canada.
CSA is a Canadian Safety Association also based on NEC and CSA-US marking as per CSA is accepted by US. However, I have seen some electricians and/or store inspector refusing to touch any fixture or allowing an installation if it does not have a "UL" marking on it. I don't want to take the risk and certify under the marking that's accepted in US.
We have a design that is very close to a set up of a Beauty/Hair Salon. We are building a table which will have 4 receptacles for hair dryers and curling irons and 6 receptacles for everything else e.g phone chargers, ipad chargers etc.
Running two separate circuits of 20A each will still not give me the current I need to satisfy full load condition and UL-962 caps out at 2 hardwired inputs.
Does anyone have any idea of which UL-Code applies to Salons? and/or help me understand how they are wired? is it a single line going to large breaker switch of 40/60A or does each plug have its own 20A line going to the breaker panel?
UL-962 is what directly applies to type of work we typically do but to provide the client with what they are looking for I am leaning towards following a UL-Code that applies to beauty Salons but I don't exactly know which one directly applies...
Thank you
I am aware that UL is accepted across US as well Canada.
CSA is a Canadian Safety Association also based on NEC and CSA-US marking as per CSA is accepted by US. However, I have seen some electricians and/or store inspector refusing to touch any fixture or allowing an installation if it does not have a "UL" marking on it. I don't want to take the risk and certify under the marking that's accepted in US.
We have a design that is very close to a set up of a Beauty/Hair Salon. We are building a table which will have 4 receptacles for hair dryers and curling irons and 6 receptacles for everything else e.g phone chargers, ipad chargers etc.
Running two separate circuits of 20A each will still not give me the current I need to satisfy full load condition and UL-962 caps out at 2 hardwired inputs.
Does anyone have any idea of which UL-Code applies to Salons? and/or help me understand how they are wired? is it a single line going to large breaker switch of 40/60A or does each plug have its own 20A line going to the breaker panel?
UL-962 is what directly applies to type of work we typically do but to provide the client with what they are looking for I am leaning towards following a UL-Code that applies to beauty Salons but I don't exactly know which one directly applies...
Thank you