I have several existing structures that have CSST gas piping installed in the buildings, in each case the structures are Condo buildings with separate gas meters for each tenant and public service. The CSST is not bonded other than by the EGC (i.e. gas furnace). NEC states that this is acceptable in 250.104 (B). However, 110.3 (B) supersedes this, the manufactures listed and labeling instructions state "This bonding point must be in as close proximity to the electrical panel as possible; close proximity of the bonding point to the gas meter is also desirable if possible. The wire gauge for bonding must be sized, at a minimum, for the full amperage available through the electrical service (per NECR) and no smaller than a 6 AWG copper wire." In addition NFPA 54 7.13.2 also states that it should be bonded.
Here are my questions as it pertains to an existing installation: a) is it required to go back and install the bond on a structure that this was installed before the changes and additions were made by the manufacture or NFPA 54? b) Sizing of the bonding conductor, how should this be sized; by the size of the main service for the building or by each tenants service? c) lastly, my intent is to use the building steel as the bonding point and setting a ground plate at the meter racks (81 meters totals, arranged on 4 racks) how do I go about sizing the bonding conductor to the steel, and can I run a continuous jumper on each rack landing it on the tenant side of each meter, if so how do I size that bonding conductor?
This is a thorn in which I want to remove, any help and input would be greatly appreciated on this subject.
Thank you,
Here are my questions as it pertains to an existing installation: a) is it required to go back and install the bond on a structure that this was installed before the changes and additions were made by the manufacture or NFPA 54? b) Sizing of the bonding conductor, how should this be sized; by the size of the main service for the building or by each tenants service? c) lastly, my intent is to use the building steel as the bonding point and setting a ground plate at the meter racks (81 meters totals, arranged on 4 racks) how do I go about sizing the bonding conductor to the steel, and can I run a continuous jumper on each rack landing it on the tenant side of each meter, if so how do I size that bonding conductor?
This is a thorn in which I want to remove, any help and input would be greatly appreciated on this subject.
Thank you,