CSST bonding

Status
Not open for further replies.

geochurchi

Senior Member
Location
Concord,NH
Occupation
Retired electrician
Hi All, couple of questions,first what is the lastest requirement for bonding CSST?also what are the code requirements for GFCI receptacle's on a deck?:?
GC
 
Hi All, couple of questions,first what is the lastest requirement for bonding CSST?also what are the code requirements for GFCI receptacle's on a deck?:?
GC

Bonding of CSST is not an NEC thing but rather a listing issue. If the CSST manufacturer instructions call for it then do so in a manner that complies with those instructions. Not all CSST requires "special" bonding.
For receptacles on decks see 210.50(E)(3).
 