darkenergy
Member
- Location
- Weirton WV 26062
- Occupation
- semi-retired electrician
… Probably not proper, but my way of conveying a headache that is radiating to all parts of my body. Concerning CSST.
Scenario: Grounding Electrode; copper water line entering building, 10 foot buried, etc., have to use it. Grounding electrode conductor (GEC). #4 copper (0000 aluminum service conductor size) One continuous piece, (CAD weld™ and irreversible mechanical crimps aside) from neutral bus to water pipe. While I'm on this topic, (waterline within 5 feet of where it enters the building), it is also my understanding (may be a poor choice of words!) That if you hit the 'street side' of the meter, you are allowed to install additional approved waterline clamps and 'jumper' back around the meter to the customer side. If you land on the customer side the same scenario is a no go, and that is where (at lest one example) the irreversible mechanical crimp/Cadweld™ requirement kicks in? T/F? just throwing this out there, but personally, I always tried to get as close to where it comes through the wall as possible. Never had one actually break while I was sanding the pipe clean at the connection point, but I have buddies who have. it became the scariest part of the job, since the local utilities now do the disconnect/reconnects. As an additional side note, for a long time I have been putting Anti-ox on the pipe/clamp face, and a healthy glob on the end of the wire I stick into the terminal on the clamp. Not a requirement, but I have been back to jobs done many years ago where everything was completely encrusted, figured it couldn't hurt going forward.
Yes, there is a green screw in it (neutral bar) . Why does the screw have to be green? To the best of my abilities to determine, it is because that is the color the inspector looks for/easy to find. Any further clarification would be greatly appreciated… But I digress.
On second thought while I'm on the topic, it is my understanding if you land the grounding electrode conductor to the equipment ground bus (mounted directly to the shell) you must use a wire type jumper 'appropriately sized' between the neutral and the equipment grounding bar, in this case #4 copper. It is also my understanding that you can land ANY branch circuit equipment ground to this bar (directly mounted to the shell), it is 'listed and approved ' for that application. it is only when a grounding electrode conductor is put there that the wire type jumper requirement kicks in . T/F On That Would Be Appreciated As Well.
'Approved/listed' terminations, connectors, etc. everywhere. GEC passes through one of said devices mounted on natural gas line. 110.12 always applies. I would posit that any ground/bond required could be on the single (GEC) conductor if the physical arrangements of said devices/equipment allow, the grounding electrode conductor being sized appropriately of course. T/F ON THAT AS WELL IF YOU WOULD PLEASE!
Legit or not? That is the question.
From the AGA (American gas Association)
A 2017 (revision 9-06-17) says "a direct bond consists of a listed grounding clamp and separate conductor run from the gas piping to the grounding electrode system"
The 2021 NFPA 54; 7.12; ELECTRICAL BONDING AND GROUNDING THROUGH 7.13; ELECTRICAL CIRCUITS (inclusive) encompasses less than half of page, column wise in aggregate. The little asterisks refer you to appendix A.
to the best of my abilities to read, nothing anywhere mentioned above (in the 2021 NFGC) specifically states 'separate conductor' and only refers you to NFPA 70 (National electric code 2017 in my jurisdiction )
EGC (equipment ground conductor) provisions; 250.122 relating to branch circuits serving gas utilization devices notwithstanding, this is only in reference to the yellow CSST. As far as I can tell. I'm sure the black is always professionally installed.
I could go on and on for pages… Because I use Dragon dictate software, speech to text. With that being said, I try to proofread but sometimes not so well so I apologize for any nonsensical words/Arrangement/lack of clarity. I have looked high and low intermittently for years (I'm sometimes prone to slight exaggeration) but quite honestly/earnestly for the last week or so and can find no definitive answers.
I welcome your criticism/critique/opinions, all will be appreciated!
Thank you all for your time if you would care to give any guidance/corrections/advice.
I figured by now there would be something definitive in at least the National fuel gas code if not the national electric code. Maybe if all the people involved were in the same organization…? Free coffee and doughnuts on/in a prepaid trip to Hawaii may develop a consensus?
Thank you again, Willy
Scenario: Grounding Electrode; copper water line entering building, 10 foot buried, etc., have to use it. Grounding electrode conductor (GEC). #4 copper (0000 aluminum service conductor size) One continuous piece, (CAD weld™ and irreversible mechanical crimps aside) from neutral bus to water pipe. While I'm on this topic, (waterline within 5 feet of where it enters the building), it is also my understanding (may be a poor choice of words!) That if you hit the 'street side' of the meter, you are allowed to install additional approved waterline clamps and 'jumper' back around the meter to the customer side. If you land on the customer side the same scenario is a no go, and that is where (at lest one example) the irreversible mechanical crimp/Cadweld™ requirement kicks in? T/F? just throwing this out there, but personally, I always tried to get as close to where it comes through the wall as possible. Never had one actually break while I was sanding the pipe clean at the connection point, but I have buddies who have. it became the scariest part of the job, since the local utilities now do the disconnect/reconnects. As an additional side note, for a long time I have been putting Anti-ox on the pipe/clamp face, and a healthy glob on the end of the wire I stick into the terminal on the clamp. Not a requirement, but I have been back to jobs done many years ago where everything was completely encrusted, figured it couldn't hurt going forward.
Yes, there is a green screw in it (neutral bar) . Why does the screw have to be green? To the best of my abilities to determine, it is because that is the color the inspector looks for/easy to find. Any further clarification would be greatly appreciated… But I digress.
On second thought while I'm on the topic, it is my understanding if you land the grounding electrode conductor to the equipment ground bus (mounted directly to the shell) you must use a wire type jumper 'appropriately sized' between the neutral and the equipment grounding bar, in this case #4 copper. It is also my understanding that you can land ANY branch circuit equipment ground to this bar (directly mounted to the shell), it is 'listed and approved ' for that application. it is only when a grounding electrode conductor is put there that the wire type jumper requirement kicks in . T/F On That Would Be Appreciated As Well.
'Approved/listed' terminations, connectors, etc. everywhere. GEC passes through one of said devices mounted on natural gas line. 110.12 always applies. I would posit that any ground/bond required could be on the single (GEC) conductor if the physical arrangements of said devices/equipment allow, the grounding electrode conductor being sized appropriately of course. T/F ON THAT AS WELL IF YOU WOULD PLEASE!
Legit or not? That is the question.
From the AGA (American gas Association)
A 2017 (revision 9-06-17) says "a direct bond consists of a listed grounding clamp and separate conductor run from the gas piping to the grounding electrode system"
The 2021 NFPA 54; 7.12; ELECTRICAL BONDING AND GROUNDING THROUGH 7.13; ELECTRICAL CIRCUITS (inclusive) encompasses less than half of page, column wise in aggregate. The little asterisks refer you to appendix A.
to the best of my abilities to read, nothing anywhere mentioned above (in the 2021 NFGC) specifically states 'separate conductor' and only refers you to NFPA 70 (National electric code 2017 in my jurisdiction )
EGC (equipment ground conductor) provisions; 250.122 relating to branch circuits serving gas utilization devices notwithstanding, this is only in reference to the yellow CSST. As far as I can tell. I'm sure the black is always professionally installed.
I could go on and on for pages… Because I use Dragon dictate software, speech to text. With that being said, I try to proofread but sometimes not so well so I apologize for any nonsensical words/Arrangement/lack of clarity. I have looked high and low intermittently for years (I'm sometimes prone to slight exaggeration) but quite honestly/earnestly for the last week or so and can find no definitive answers.
I welcome your criticism/critique/opinions, all will be appreciated!
Thank you all for your time if you would care to give any guidance/corrections/advice.
I figured by now there would be something definitive in at least the National fuel gas code if not the national electric code. Maybe if all the people involved were in the same organization…? Free coffee and doughnuts on/in a prepaid trip to Hawaii may develop a consensus?
Thank you again, Willy