CSST, Concerns over Lightning Strikes

Status
Not open for further replies.

joe tedesco

Senior Member
Corrugated Stainless Steel Tubing for Fuel Gas Distribution in Buildings and Concerns over Lightning Strikes

August 2007
Executive Summary

As the result of recent legal actions related to a potential for physical damage caused by lightning, manufacturers of corrugated stainless steel tubing (CSST) agreed to a settlement that, in part, places new requirements on the installation of their gas piping products. This paper provides background information on CSST and the actions taken by the manufacturers to address these concerns.

http://www.toolbase.org/pdf/techinv/csst_lightningconcerns.pdf
 
First it appears that in place of bonding this product should be banned. Second, the problem of costs comes into play...the responsibility of installing the bond should fall to the contractor that has installed the light weight easily damaged gas piping system, not the electrical contractor.
Don
 
don_resqcapt19 said:
First it appears that in place of bonding this product should be banned.
I must respectfully disagree. It is not clear that with the proper bonding CSST is any more vulnerable to lightning strike than iron pipe. But suppose that it is, that still doesn't mean it should be banned. For example, my understanding is that CSST is more resilient in an earthquake, by being flexible and installed in a way that it is not tightly coupled with the structure. Then it would be a trade off, with CSST possibly a better choice in areas of high seismic risk, and iron pipe possibly a better choice in areas of high lightning risk.

Yours, Wayne
 
don_resqcapt19 said:
First it appears that in place of bonding this product should be banned. Don

I absolutely agree. If this product is that fragile, I sure wouldn't want it run all throughout my house buried in walls and ceilings just waiting for a fault that will cause an explosion. Besides that, it's just plain bad looking coming from the meter and running into the house. It's way too thin to be exposed to the elements the way I've seen it installed.
 
Wayne,
Then it would be a trade off, with CSST possibly a better choice in areas of high seismic risk, ...
That is something that I don't really think about here in northern Illinois, but we probably should. I just think it is a very fragile product. Do the plumbing codes have anything like our 300.4 for protection of this product?
Don
 
don_resqcapt19 said:
Do the plumbing codes have anything like our 300.4 for protection of this product?
Don

Not from what I have seen.

I just ran into some of this product in a steel truss building.

The gas line was snaked up between the ribs of the roof decking like we snake MC cable.

Of course starting in 2008 I will not be able to run electric lines up in the ribs but I guess a gas line is OK.
 
I am kind of suprised this problem with lightning was not discovered in the testing stages of this product, before it was put into production, does anybody know what they plan to about all the jobs that are not bonded as per there bulletin, I don't know if it should be banned, maybe just taken off the market until all the bugs are worked out
 
stickboy1375 said:
I've yet to see a house explode... anyone else?

No I have not but I believe the number of buildings that did blow up where behind the lawsuit that resulted in the new bonding requirements.:D
 
iwire said:
No I have not but I believe the number of buildings that did blow up where behind the lawsuit that resulted in the new bonding requirements.:D


:D I would really like to see a report on how many actually did, and how they determined it was caused from lightning and CSST.
 
stickboy1375 said:
:D I would really like to see a report on how many actually did, and how they determined it was caused from lightning and CSST.

Follow the link in post #1, I have not looked but I bet all that info is in there. :smile:
 
I really doubt that any buildings blew up...the current that burned the hole in the line most likely ignited the gas at the same time...no explosion, just fire.
I wonder how much current it takes to melt a hole in the line?
Don
 
Plumbers love this stuff. It has all but replaced black pipe around here, and from my own observations it's taken over other parts of the country as well.
 
Peter,
Plumbers love this stuff.
Why would a plumber like it?...it just reduces the manhours required for a project and the demand for plumbers. Same with electricians and MC.
Don
 
don_resqcapt19 said:
Peter,

Why would a plumber like it?...it just reduces the manhours required for a project and the demand for plumbers. Same with electricians and MC.
Don

Don that is a very different view point then contractors have out here.

Get in, get out, move on to the next job.

More jobs worked, more money made.
 
Bob,
on that is a very different view point then contractors have out here.
I didn't say contractors...I am talking about the worker, but the contractors should feel the same way. If the code requires a more labor intensive installation the job costs more and there should be more profit.
Don
 
don_resqcapt19 said:
Do the plumbing codes have anything like our 300.4 for protection of this product?
Not sure about the plumbing code, but the installation instructions of the CSST product I have used address protection from puncture. The basic strategy is to keep it 3" from the edge of framing, or to loosely hang the CSST so that if anything pushes on it it can deflect to at least a 3" distance. Where the CSST is constrained close to the edge of framing, you need to protect it with a heavy striker plate or a spiralwound conduit.

Cheers, Wayne
 
Here is a picture of the required striker plates from Gastite.

strikerplatesbgwt1.jpg


They are quite a bit larger then standard nailplates. They are required to extend past the bottom and top plates at least three inches.

Chris
 