7.13.2 CSST. CSST gas piping systems shall be bonded to the electrical service
grounding electrode system at the point where the gas service enters the building.
The bonding jumper shall not be smaller than 6 AWG copper wire or equivalent.
Is the bonding done only one point, where the pipe enters the building?
This building has hard pipe thruout except small sections of CSST flex pipe that was used as "jumpers" between sections of hard pipe.
should these sections be jumped with a bonding jumper, or is the bond on the hard pipe at the entrance sufficient?
grounding electrode system at the point where the gas service enters the building.
The bonding jumper shall not be smaller than 6 AWG copper wire or equivalent.
Is the bonding done only one point, where the pipe enters the building?
This building has hard pipe thruout except small sections of CSST flex pipe that was used as "jumpers" between sections of hard pipe.
should these sections be jumped with a bonding jumper, or is the bond on the hard pipe at the entrance sufficient?