ct 800 amps

charlyboy

New User
Location
texas
Occupation
Mant Tech
Good afternon , my cuestion is that is possible install 800 amps disconect without fuses anter CT box meter ?,, or have to be fused/
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So you have service point>CT's>800 unfused disconnect? Where is the service OCPD located?
 
Technically you could. As Rob said, you still need a service OCPD(s) and it must be "immediately adjacent thereto". So you could have, say, an 800 amp NF disco, and that feeding (4) 200A fused discos, but why would you want to do that? You could have the 4 fused discos and just get rid of the NF disco. The only reason I can think of is to use double throw switch for say a generator connection. What are you trying to accomplish?
 