S Sparky3601 Member Location Windsor, CO Mar 17, 2017 #1 Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft
Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Mar 17, 2017 #2 Sparky3601 said: Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft Click to expand... Yes, 230.43. You would have to pay attention to the extra bonding requirements though. Some POCOs may have an issue with this even though the NEC permits it.
Sparky3601 said: Is it acceptable to use LFMC on the load side of a CT Cabinet, to the line side of the first means of disconnect? The LFMC run is less than 6ft Click to expand... Yes, 230.43. You would have to pay attention to the extra bonding requirements though. Some POCOs may have an issue with this even though the NEC permits it.
S Sparky3601 Member Location Windsor, CO Mar 20, 2017 #3 Thank you for the reply. I knew 230.43 permits it, I wasn't sure if there was an "exposed to physical damage" article that I was overlooking
Thank you for the reply. I knew 230.43 permits it, I wasn't sure if there was an "exposed to physical damage" article that I was overlooking