I have a situation that has arose on the use of home made ct cans,
We are a controls contractor and have two EC state license's, one of our tech was installing a new energy meter inside the panel in question. When he was complete he reinstalled the cover and a tek screw penetrated the wire and resulted in a direct short. i have attached in his words what happened.
"The following incident took place on Jan. 21, 2010 @ Medical Technology Buildings, chiller plant @ 12:00 PM. After finishing the installation of a Veris Energy meter, I was putting the cover back on the pull box attached to the switch gear. While screwing one of the tek screwing back into the enclosure, the screw penetrated the insulation of one of the A phase conductors. This resulted in a direct short to ground causing damage to the conductor and the edge of the enclosure. This accident did not cause injury to anyone, only the above mentioned equipment. I directly went to Gordy, the foremen for Electric co, to inform him of what just happened. We looked @ the enclosure and got Brad the G.C. to see how to proceed. Brad, from gc, instructed Gordy to replace the wire. This will result in a FPL shut down as these conductors go directly to the transformer. If any other info. is required please call."
My question here is it required that the conductors be in a UL raceway or is that up to the engineer to accept?
Also can the use of none UL equipment be used with state money involved?
We are a controls contractor and have two EC state license's, one of our tech was installing a new energy meter inside the panel in question. When he was complete he reinstalled the cover and a tek screw penetrated the wire and resulted in a direct short. i have attached in his words what happened.
"The following incident took place on Jan. 21, 2010 @ Medical Technology Buildings, chiller plant @ 12:00 PM. After finishing the installation of a Veris Energy meter, I was putting the cover back on the pull box attached to the switch gear. While screwing one of the tek screwing back into the enclosure, the screw penetrated the insulation of one of the A phase conductors. This resulted in a direct short to ground causing damage to the conductor and the edge of the enclosure. This accident did not cause injury to anyone, only the above mentioned equipment. I directly went to Gordy, the foremen for Electric co, to inform him of what just happened. We looked @ the enclosure and got Brad the G.C. to see how to proceed. Brad, from gc, instructed Gordy to replace the wire. This will result in a FPL shut down as these conductors go directly to the transformer. If any other info. is required please call."
My question here is it required that the conductors be in a UL raceway or is that up to the engineer to accept?