So I'm replacing the normal feed for an ATS. It's current fed with 4/0 type CT cable, protected by a 150A breaker. This seems like a bit of an overkill to me.
Per 392.11(B)(2) it seems like I can run individual conductors of 2/0 tray-rated THHN in a ladder type tray and have it rated at 152.75A.
Is this correct? Thanks.
-John
Per 392.11(B)(2) it seems like I can run individual conductors of 2/0 tray-rated THHN in a ladder type tray and have it rated at 152.75A.
Is this correct? Thanks.
-John