I wanted to ask you a question regarding CT data and how can it be read and interpreted. I have attached an image of the CT data. So how to choose the box if I was given in the single line diagram a CT of type B for example.

Capture.jpg
 
Like the other post indicated, not sure what you question is. The chart shows ratios with 1amp secondary current. The standard in the USA is 5 amp secondary current. And it shows KW ratings. CT ratio has nothing to do with KW rating of equipment.
It is a current device and is selected to match the current rating of the supplied load. For instance, if the load is rated for a maximum of 400A then a 400:5 ratio is selected to feed a 400A full scale ammeter (0 to 5A) and would be installed on each phase of the 500MCM cable and wired thru a shorting block and an ammeter switch.
You need to google current transformers and learn the basics before you can specify these devices.
 
Table looks like IEC CT sizing information for various sizes of transformers or services. The CT specification, ratios and 1 A secondaries look like IEC.

Top row lists the transformer/load size in kVA. Right Column lists the CT type- metering or protection (X or P), the size (10VA) and the accuracy.

Rows A-C list various ratios of CT's. Row A looks like dual ratio metering CT's, 600:1 or 400:1. Class X is usually a higher accuracy for metering pruposes.

Row B look like dual ratio protection CT's, 100:1 or 50:1. The 5P20 rating means a protection CT capable of delivering 20 times rated current (20A) with a 5% accuracy. (If I recall the specs correctly).

Row C are single ratio protection CT's. The ratios look like they might be for 400V secondary CT's for the given size of the transformer in the top row.

Could be a chart for sizing CT's for transformers. A is for HV metering, B for HV protection and C for LV protection. (Wild guess).
 