M mstrlucky74 Senior Member Location NJ Nov 6, 2017 #1 Drawing showing 3#3’s in 1-1/4” fed from 3P 200A switchfused at 100A to VFD then to disconnect at cooling tower? How could there beonly 3 wires? Thanks.
Drawing showing 3#3’s in 1-1/4” fed from 3P 200A switchfused at 100A to VFD then to disconnect at cooling tower? How could there beonly 3 wires? Thanks.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 6, 2017 #2 3 phase, no neutral with conduit as the EGC.
Jraef Moderator, OTD Staff member Location San Francisco Bay Area, CA, USA Occupation Electrical Engineer Nov 7, 2017 #3 infinity said: 3 phase, no neutral with conduit as the EGC. Click to expand... It's a bad IDEA to use the conduit as the EGC when feeding a VFD, but not a code violation. The NEC is a set of minimum requirements, not a design guide...
infinity said: 3 phase, no neutral with conduit as the EGC. Click to expand... It's a bad IDEA to use the conduit as the EGC when feeding a VFD, but not a code violation. The NEC is a set of minimum requirements, not a design guide...