James Perry
Member
When installing ground fault protection on an existing 400 amp breaker, the engineer wants a CT on the neutral.Should the current flow arrow or dot be reversed from the phase CTs? System is 120/208.
It needs to be mounted/wired per the GF relay manufacturer's instructions. I know it sounds like a cop-out, but this is really all that matters.When installing ground fault protection on an existing 400 amp breaker, the engineer wants a CT on the neutral.Should the current flow arrow or dot be reversed from the phase CTs? System is 120/208.