We have install multiple 1 1/2", 2", and 2 1/2" galvanized flex(greenfield) down into existing walls that are to be used by the equipment manufacture as chases for their equipment wiring.(that will be installed by their installers) The AHJ referenced article 517.13 and said that we are not allowed to use ANY galvanized flex in patient care areas. The main feed for the equipment is in emt all the way from MDP over to the disconnect in the room except for a 6' tail that goes from the disconnect over to the manufacturers PDU that is on rollers. This is a list of my questions:
1. Would a CT exam room be classified as a patient care area?
2. Would these chases be classified as branch circuits?
3. Is the AHJ correct in this statement?
4. If not what is the best way to plead my case?
Thanks in advance