How should I calculate the ratio of a current transformer to be installed at the solidly grounded neutral of a power transformer?
I am calculating the CT ratio for protecting a power transformer against over-currents. The CT of each phase (in the secondary side) was calculated based on the nominal current of the transformer with a nominal power of 30 MVA @ 6.6 kV, so the CTs ratio is 3000:1
I hope I'm thinking it right (if not, you will tell), but since in a balanced three-phase system the current through the neutral should be zero, the continuous current rating of the neutral CT could be defined as a percentage of the continuous current rating in the lines. So if it applies, which should be the maximum percentage of the secondary side nominal current that I should use, maybe a percentage of maximum phase imbalance expected/allowed)?
If the former analysis does not apply, how do you define the radio of the neutral CT?
Thank you in advance.
I am calculating the CT ratio for protecting a power transformer against over-currents. The CT of each phase (in the secondary side) was calculated based on the nominal current of the transformer with a nominal power of 30 MVA @ 6.6 kV, so the CTs ratio is 3000:1
I hope I'm thinking it right (if not, you will tell), but since in a balanced three-phase system the current through the neutral should be zero, the continuous current rating of the neutral CT could be defined as a percentage of the continuous current rating in the lines. So if it applies, which should be the maximum percentage of the secondary side nominal current that I should use, maybe a percentage of maximum phase imbalance expected/allowed)?
If the former analysis does not apply, how do you define the radio of the neutral CT?
Thank you in advance.