Hello,
I'm new to the forums, but I've used this forum to find the neutral current in a 3-phase unbalanced system. I figured this would be a good place to ask the question. I hope that I can make sense of it in text because it's kind of hard to explain. I've attached a poorly drawn diagram trying to graphically show what I'm asking as well.
Basically, I work at an electric utility company and we use meters rated for 200 amps. If the current through the meter is greater, we use CTs and calculate the demand based on the CT ratio. Well we had an issue the other day where the C-phase CT lead was going to the B phase current lead on the meter. The B phase CT lead was going to the C phase current lead on the meter. Basically the two current leads going to the meter were swapped for B and C phase. The correct voltage leads from the transformer all went to the correct voltage leads on the meter and the A phase current lead was correctly wired as well.
My manager came in to ask me a question about this. I've scanned my three engineering books from college and can't figure out if what I'm doing is correct or not. 3 phase power (real) is define as:
P = V*I*cos(theta) for each phase (where theta is the angle between the voltage and the current) and the total power is defined as:
Ptotal = Va*Ia*cos(thetaA)+Vb*Ib*cos(thetaB)+Vc*Ic*cos(thetaC)
Lets assume Va=Vb=Vc, Ia=Ib=Ic, and our power factore is 1.0. The voltage phase angle between phases A, B, and C are 120 degrees. The same is true for the current.
In my attached example, I've setup an example problem with some random numbers. I defined the voltage phase angles as 0 degrees, -120 degrees, and +120 degrees for A, B, and C respectively. I've assumed that we calculated the current phase angle on A phase is 40 degrees. Therefore, the current phase angles for B and C have to be -80 degrees, and 160 degrees respectively (120 degrees apart).
Now, if we use the Ptotal formula above we get (this is with the B and C current leads swapped):
Ptotal = V*I*cos(0 - 40 degrees)+V*I*cos(-120 - 160 degrees)+V*I*cos(120 +80 degrees)
**Notice I used the normal calculation for A phase power since the voltage and current leads are correctly wired. However, I used B phase voltage phase angle and C phase current phase angle for the calculation of B phase theta since the connections are swapped going to the meter.
--> Ptotal = V*I*cos(-40 degrees)+V*I*cos(-280 degrees)+V*I*cos(200 degrees)
--> Ptotal = V*I*(0.766044443 + 0.173648178 - 0.939692621)
--> Ptotal = V*I*(0) = 0 W
Is this correct? Will the meter read 0 W for the demand since the B and C phase current leads are swapped going to the meter?
I hope this makes sense. I would appreciate any help on the matter.
Thank you,
Adam
I'm new to the forums, but I've used this forum to find the neutral current in a 3-phase unbalanced system. I figured this would be a good place to ask the question. I hope that I can make sense of it in text because it's kind of hard to explain. I've attached a poorly drawn diagram trying to graphically show what I'm asking as well.
Basically, I work at an electric utility company and we use meters rated for 200 amps. If the current through the meter is greater, we use CTs and calculate the demand based on the CT ratio. Well we had an issue the other day where the C-phase CT lead was going to the B phase current lead on the meter. The B phase CT lead was going to the C phase current lead on the meter. Basically the two current leads going to the meter were swapped for B and C phase. The correct voltage leads from the transformer all went to the correct voltage leads on the meter and the A phase current lead was correctly wired as well.
My manager came in to ask me a question about this. I've scanned my three engineering books from college and can't figure out if what I'm doing is correct or not. 3 phase power (real) is define as:
P = V*I*cos(theta) for each phase (where theta is the angle between the voltage and the current) and the total power is defined as:
Ptotal = Va*Ia*cos(thetaA)+Vb*Ib*cos(thetaB)+Vc*Ic*cos(thetaC)
Lets assume Va=Vb=Vc, Ia=Ib=Ic, and our power factore is 1.0. The voltage phase angle between phases A, B, and C are 120 degrees. The same is true for the current.
In my attached example, I've setup an example problem with some random numbers. I defined the voltage phase angles as 0 degrees, -120 degrees, and +120 degrees for A, B, and C respectively. I've assumed that we calculated the current phase angle on A phase is 40 degrees. Therefore, the current phase angles for B and C have to be -80 degrees, and 160 degrees respectively (120 degrees apart).
Now, if we use the Ptotal formula above we get (this is with the B and C current leads swapped):
Ptotal = V*I*cos(0 - 40 degrees)+V*I*cos(-120 - 160 degrees)+V*I*cos(120 +80 degrees)
**Notice I used the normal calculation for A phase power since the voltage and current leads are correctly wired. However, I used B phase voltage phase angle and C phase current phase angle for the calculation of B phase theta since the connections are swapped going to the meter.
--> Ptotal = V*I*cos(-40 degrees)+V*I*cos(-280 degrees)+V*I*cos(200 degrees)
--> Ptotal = V*I*(0.766044443 + 0.173648178 - 0.939692621)
--> Ptotal = V*I*(0) = 0 W
Is this correct? Will the meter read 0 W for the demand since the B and C phase current leads are swapped going to the meter?
I hope this makes sense. I would appreciate any help on the matter.
Thank you,
Adam