jmellc
- Durham, NC
- Facility Maintenance Tech. Licensed Electrician
Looking at a job for my church, possibly having POCO set a new transformer, feeding a service for several office trailers. 1 trailer for sure has a 200A panel, 1 has a 100A panel. Other 2 are in future, probably no more than 200A each.
Meeting Sat with guy from POCO, until then I can't open existing transformer cabinet to check things out.
Our existing transformer has a 3 phase meter on a short post right next to it. I'm sure the CT's are inside the transformer. The meter base is too small for them. It is a 480, probably has capacity for the needs, but we'd have to set a 208 txf next to it, and cut across driveway, etc. Same with MDP in building. Plenty of space, but it's 480 & we don't have much space for txf there.
My thinking is having POCO set a txf at a spot within 100' where it has spare pedestals already. Set a 3 phase meter next to it and ditch over to approx ctr of trailer sites. Set up a stand there with 600A disconnect & large j box or line gutter. Parallel feed it with 2 350 MCM's & tap for each trailer with a breaker enclosure, trench out to each trailer as it arrives. Use Polaris lugs to splice taps. Drive 2 ground rods at stand. Feed 1 phase loads with AB, BC, CA, AB. I f I keep the known lighter load on AB, it should keep the loads approx equal, as C is 1 less load to start with.
Anyone see problems here? Am I overlooking anything?
My supply houses so far only have a 300A meter base. I thought 3 phase meter bases were somewhat standard, as ct's are used to give them partial current. I believe our main breaker in MDP is 1,500A, have to check again. Are
most transformer cabinets large enough to mount CT's inside, as our existing one appears to be?