CU and AL in same lug

Status
Not open for further replies.

csoc64

Senior Member
Location
northeast
Have a ground lug which indicates CU/AL. If I want to combine a copper an aluminum ground wire under the same screw, does the CU/AL reference meet the requirements of 110.14 for a "device intended for the purpose and conditions of use"?. An anti-oxidant (Noalox) will be used on the AL wire. This came up as an issue during a recent inspection where the AHJ insisted on a separate lug for each type of wire.
 
No mention was made if the lug is listed for 2 wires (that I saw).
Even if it were you generally can not mix copper and aluminum in the same port - unless specifically designed/listed for it - I don't know of any though that are designed for it.
 
Even if it were you generally can not mix copper and aluminum in the same port - unless specifically designed/listed for it - I don't know of any though that are designed for it.

i've transitioned aluminum to copper in a hypress butt splice, but the splice is rated for AL9CU,
and the dissimilar materials don't touch each other. i don't think anywhere that would be a good idea.
the material characteristics aren't gonna squish together well.
 
i've transitioned aluminum to copper in a hypress butt splice, but the splice is rated for AL9CU,
and the dissimilar materials don't touch each other. i don't think anywhere that would be a good idea.
the material characteristics aren't gonna squish together well.
Technically, they were not in the same port.:p
 