CU Bus Instead Of Splice

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
So I have an existing riser I'm intercepting( 4 sets of 4#500) and connect via pull box and new pipe/wire form dist. board. I've never seen, as the engineer/notes request as I've attached, to use a cooper bus/detail to connect the existing feeders to the new. Though you always used some sort of tap/splice block. So I assume one set of feeder terminate on lugs at the bottom of the bus and the others on the top? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    18.4 KB · Views: 1

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I would think one would just buy something off the shelf rather than trying to make something. At least it is listed that way and not something home made.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
To be honest, I don't see the word "bus" in the attached note. I only see "detail". I'm assuming the engineer wants you to provide a detail of the connections?

If the engineer does want a bussed connection, I think a "Cooper Bussed gutter" or something similar would be an off-the-shelf solution.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
To be honest, I don't see the word "bus" in the attached note. I only see "detail". I'm assuming the engineer wants you to provide a detail of the connections?

If the engineer does want a bussed connection, I think a "Cooper Bussed gutter" or something similar would be an off-the-shelf solution.

I did not even know such a thing existed. I will have to remember it in case I need something like it at some point down the road.
 

mstrlucky74

Senior Member
Location
NJ
To be honest, I don't see the word "bus" in the attached note. I only see "detail". I'm assuming the engineer wants you to provide a detail of the connections?

If the engineer does want a bussed connection, I think a "Cooper Bussed gutter" or something similar would be an off-the-shelf solution.

Cooper detail in my mind means a copper bus bar.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So I have an existing riser I'm intercepting( 4 sets of 4#500) and connect via pull box and new pipe/wire form dist. board. I've never seen, as the engineer/notes request as I've attached, to use a cooper bus/detail to connect the existing feeders to the new. Though you always used some sort of tap/splice block. So I assume one set of feeder terminate on lugs at the bottom of the bus and the others on the top? Thanks.

Basically it just a box with 4 sections of copper bus detail where you can attach the incoming and outgoing lugs. A big waste of money IMO when you could use an 8 port Polaris type connector.
 

mstrlucky74

Senior Member
Location
NJ
Basically it just a box with 4 sections of copper bus detail where you can attach the incoming and outgoing lugs. A big waste of money IMO when you could use an 8 port Polaris type connector.

Thanks. Maybe we will get the job and submit for approval on tap connectors:D and maybe the engineer will mark the submittal REJECTED:p
 

Joe Villani

Senior Member
Basically it just a box with 4 sections of copper bus detail where you can attach the incoming and outgoing lugs. A big waste of money IMO when you could use an 8 port Polaris type connector.

They make a polaris type connector that's good for 1500 amps?

I always thought they were only good for the largest terminal (wire size) at 90 degrees C ???
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
But you have to stagger the inputs and outputs.

Sometimes you don't have to do that. For example, if all the inputs are on the bottom, and all the outputs are on the top.

But you are correct in that you cannot put all the inputs on the right and outputs on the left.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree as long as you stagger them it's fine. In some people's mind the bus bar scenario is probably better.
 