Cu water line/ GEC connection

nizak

Senior Member
I have a service disconnect located on the house exterior. At that point there are 2 driven ground rods from the disconnect.

At the opposite end of the house ( 160’ there is a 1” Cu underground water line coming into the basement.

With that Cu water line being present does it need to be connected to the GE system?

Thanks
 
Yes.
if the cu line qualifies as a grounding electrode then it’s bonded within 5 ft of entry and also to GES
If not then it can bonded on any accessible location.
You would be fortunate if the cu changes to plastic outside basement to save a long run of s GEC
 
if the cu line qualifies as a grounding electrode then it’s bonded within 5 ft of entry and also to GES
If not then it can bonded on any accessible location.
I once had an interesting discussion with an inspector about this during a residential upgrade.

If we can not prove whether an existing water supply qualifies, do we treat it like it does or doesn't?
 
I once had an interesting discussion with an inspector about this during a residential upgrade.

If we can not prove whether an existing water supply qualifies, do we treat it like it does or doesn't?

Was it used as electrode previously and part of GES? That might be a good indicator. Other than that , might be hard to prove. If older and see metal pipe coming up from grade , good possibility. Why chance it? Piece of #4 or #6 cheap insurance. The very least you’ve now done is bonded interior metal piping.
 
Was it used as electrode previously and part of GES? That might be a good indicator.
Let's say the original water-pipe connection was near the panel.

Other than that , might be hard to prove. If older and see metal pipe coming up from grade , good possibility.
Can we rely on it to be an effective electrode; or, must we?

Why chance it? Piece of #4 or #6 cheap insurance. The very least you’ve now done is bonded interior metal piping.
Agreed, but it was bonded nearby before the rules changed.
 