cUL life safety loads and fire pump

Status
Not open for further replies.

BPE9

New member
Location
Glen Ellyn
Hello Group,

My first post.

Can anyone tell me if the life safety and fire pump feeders need to be isolated(UL 1558)? I'm working on a project and the engineer specified UL891 and thermomagetnic for the fire pump.

Thanks.
 
700.10(B) makes reference to seperate vertical SWBD sections but indicates no isolation is required. Of course SWBDs in general don't have 1558 type isolation, although it could be special ordered.
 