Calculation Dilemma:
In working with 120/208v systems, when calculating a single phase load on a circuit, the Power (watts) = Voltage(120v) * Current(Equip. rating) (ex. 120v * 4A = 480W)
If the equip. is two pole which calc. would be correct per leg, that is:
120v * 4A = 480W per connected leg or,
208v * 4A = 832vA
I've tried to understand this as Watts and KVA are not exactly the same in that KVA takes into consideration the pf.
Joshua
Raleigh, NC
[ April 01, 2003, 10:18 AM: Message edited by: jobrafo ]