I have a twinned furnace each requiring its own 20A ckt. The FLA for each is 12.5A. The current wiring is 3ea #10, (H, N, G). Can I install another hot and neutral #10 thhn and be within code in the same raceway? The existing panel is a 4w 3ph 208 wye connected system and the existing raceway is 3/4" EMT.
According to 310.15 (B) (3) (b) the neutral is considered a current carrying conductor making (4) hot wires and one ground in a 3/4" raceway. I am sure there needs to be a calculation done for deration on the cable, but I get lost in the translation......lol. Can anyone offer some help on this?
According to 310.15 (B) (3) (b) the neutral is considered a current carrying conductor making (4) hot wires and one ground in a 3/4" raceway. I am sure there needs to be a calculation done for deration on the cable, but I get lost in the translation......lol. Can anyone offer some help on this?