Current carrying conductors

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Fair number of variables... insulation type, ambient, length etc.
But assuming THWN-2 insulation and greater than 24" you can get 16 #10s. If all were current carrying the derating would be 50% so the 90° adjustment would be 20 amps.
Solid or stranded would be the same.
 