hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have an on going argument with local inspector regarding neutral is current carrying. I am feeding 11 circuits, 120V, single phase: 1 phase 1 neutral from 120/208V three phase 4 wire panelboard in one conduit with one common EGC. I am counting 11 current carrying conductors all phase.
NEC 2014 Article 310.15(B)(5)(a): neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
In my case I have neutral conductor that carries unbalanced current from other conductors. However, inspector seems to disagree says current carrying conductors I have are 22 neutral is counted as current carrying but did not say why even though asked multiple times.
I have read from previous post charts that indicate inspector maybe correct but 310.15(B)(5)(a) specifically says neutral is not counted when carrying unbalanced current from other circuits.
Is inspector correct? If so then under what argument is he correct?
NEC 2014 Article 310.15(B)(5)(a): neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a).
In my case I have neutral conductor that carries unbalanced current from other conductors. However, inspector seems to disagree says current carrying conductors I have are 22 neutral is counted as current carrying but did not say why even though asked multiple times.
I have read from previous post charts that indicate inspector maybe correct but 310.15(B)(5)(a) specifically says neutral is not counted when carrying unbalanced current from other circuits.
Is inspector correct? If so then under what argument is he correct?