A customer of mine has a manufacturing facility. There are two 200 amp 120/208 services beside each other. The AHJ said I could use the same set of ground rods for both services. I added a 400 amp single phase service at the other end of the building for some new equipment. The AHJ had me bond the 2 grounding electrode systems together. As a precaution I took an amp reading on the #2 bare cu that ran between the services. Amps=0. I then checked the #6 conductors from the 3 phase services that ran to the pair of ground rods. Amps=15. If I separate the #6 conductors from the shared rods there is no voltage between them. How can you get current flow without voltage present. I omitted the faulty test equipment by using 2 different meters and amp probes tested elsewhere. I believe the current flow is from introducing a parallel path between the 2 neutrals with the #6 conductors terminating together at the shared rods, but the lack of a voltage when I separate them is confusing to me.