Say we have a 208Y/120V system and supply a 208V to 240V autotransformer from lines A-B, with B' the derived line at 240V from A. Then I worked out that B' is 149V from N. (The 32V boost B-B' is 30 degrees out of phase from N-B.)
But what are the current flows if B' faults to N? Is treating a fault like a resistive load reasonable? If so, I expect that I should be able to work out the unknown current phasors in lines A and B just by applying KCL repeatedly (I need to try that). Is there an easier way?
Cheers, Wayne
But what are the current flows if B' faults to N? Is treating a fault like a resistive load reasonable? If so, I expect that I should be able to work out the unknown current phasors in lines A and B just by applying KCL repeatedly (I need to try that). Is there an easier way?