If I have a 120v heater and I cut the Neutral so current can't make its way back to source will the hot wire still have any current on it. From how I understand it the answer is no as it won't trip a GFCI breaker as there is no imbalance. Let me know what you think thank you.
 
Basically, what I am asking is if I intentionally open the neutral and put my amp clamp on the hot with a load attached will I see current on the hot.
 
Certain conditions you could have a slight reactive current due to the hot conductor capacitive coupling to a neutral or a ground. But that would not be enough to matter.
 